Hello Robert
Thanks for the hint!
Here is the attachment:
Modbus/TCP includes a Unit ID field, which is used to address multiple Modbus slaves at a single IP address. Unfortunately, some first generation software drivers assumed a single slave at each IP and always set the Unit ID field to 0. This causes the Device server problems because it requires the Unit ID for the Modbus/RTU “Slave Address”. To support these older applications, the Device Server allows you to force a fixed address for Modbus/RTU and Modbus/ASCII, but note that this restricts you to a single serial slave
device per Device Server. Setting this value to 0 causes the Device Server to use the Modbus/TCP Unit ID as received. Setting it to any other address causes the Device Server to always use the set value as a fixed address.