Hi Bjorn,
Below the RemTrans objects you have to place a buffer object which will contain the message. If you are sending, you fill in the buffer object in the RemTransSend plc window, and if you are receiving you read the buffer object and unpacks the messag in the RemTransRcv plc window.
As your messages only contains integers, you can use a IArray100 as a buffer object. You then don't have to declare a special struct for the message. You declare the Da1 pointer with
[code:1]classdef Da1 IArray100;[/code:1]
in the DataArithm code and use Da1->Value[0], Da1->Value[1] etc to access the message data.
Note also that the message normally contains a header, which can be removed by setting DisableHeader in the RemNode object.
If you don't view the plant in the plc editor, you can select objects in the configurator and connect to function objects in the plc editor.
/Claes