Hi Marc, hi jds
it is exactly as jds pointed out in the
post a year ago. The project I received actually contains two nodes (BYS and bys) that have identical names except for the lower case.
What's a bit weird is that it didn't help that I adjusted the simulation node to my training environment (prvwtrain03). The scan time still remained at twice the value. Only inserting the project dump and loadfile of the directory into a new project solved the problem as described in my original post.
I have carried out further investigations:
To do this, I set up another runtime system (Prd2: 64-bit version ProviewR 5.9.0-2 on RPI 4B) and did a force build. On the Prd2 the times were correct, nothing changed for the simulation system prvwtrain03 (times still wrong).
I then deleted the runtime system Prd1 and did another force build and lo and behold, the error is gone. Of course, this is easier than the way around via a new project.
I thank you for your advice and consider the problem solved - even if I didn't understand all the details (I never saw a second PLC process). The main thing is that the problem can be reproduced and avoided.
Super system, super forum - Using ProviewR you'll never walk alone!
/Martin