Thanks for you quick response... i get better support here than I get for my expensive Beckhoff TwinCAT...
You should connect the channel to a signal of type Ii in the planthier.
Ok
Also you should have connected the slave and the modules to a plcthread-object and the Process should be '1'.
Ok
You can see what is read from the module in the Input-area in the slave object. Attribute named Inputs. Do you see any values there ?
No value here.
Also make sure the Address is correct of the area to read. Sometimes you should reduce it by 1 compared to what the documentation for your i/o says.
Ok
You should also check the status on the input-module. Is it OK ?
Ok
Note also that there is a new Proview-package to download since the 2 of june. This has some bugfixes in the Modbus-area.
I will try with the new version.
I will keep you informed about the sitation after i upgraded.
Thanks and best regards
Martin